The answer, of course, is that you shouldn't use aluminum at all.jcash wrote:What size aluminum conductor should I use? Service line for a poultry house, 120/240 volt service, 155' from trasformer pole to load site. Estimated load is 190 amps and I can only have a 1.5% voltage drop.
I am using 4/0 welding cable; what is the equilivent in "HCM" size?Knight wrote:The answer, of course, is that you shouldn't use aluminum at all.jcash wrote:What size aluminum conductor should I use? Service line for a poultry house, 120/240 volt service, 155' from trasformer pole to load site. Estimated load is 190 amps and I can only have a 1.5% voltage drop.
The answer is 350 kCmil wire. tough to find. You'll want to use 4/0 copper in real life.
Check out http://www.electrician.com/vd_calculator.html for a handy voltage drop calculator.
http://www.powerstream.com/Wire_Size.htm has a good reference for finding resistivity of copper wire. all you'll need to remember is that aluminum wire has a k 1.64 times that of copper, and you should be able to convert.
I'm not sure what "HCM size" is. AWM 4/0 wire (American Wire Gauge) is 120 mm for metric standard.peter upton wrote:I am using 4/0 welding cable; what is the equilivent in "HCM" size?